JoeB wrote:
Those of you that list a category and incident energy on the arc flash label, what do you call the category?
Level
PPE Level
Category
HRC < pretty sure that one is not a good idea.
Your question is somewhat unclear. 70E, in Article 130, tells us equipment must be labeled with the following:
1) ONE of the following:
a. Available incident energy and the corresponding working distance
b. Minimum arc rating of clothing
c. Required level of PPE
d. Highest Hazard/Risk Category for the equipment.
2) Nominal system voltage
3) Arc flash boundary.
If by "What do you call the category," you are refering to the nomenclature on the label, you'd call it "Hazard / Risk Category:"... not sure what you mean by "pretty sure that one is not a good idea" but I'm guessing you're thinking an abbreviation isn't a good idea. You'd be right, in my opinion.
The attached image is a label on some equipment at a petrochemical refinery I frequent. It should help you out a bit, I'd guess.