mike01 wrote:
In reviewing the 2015 70E as it relates to our company’s label updates, typically in the past we listed the incident energy along with the system voltage and boundary and the appropriate HRC / PPE category for the equipment based on the calculated I.E. However looking over the revised 70E 130.5[C] indicates that the results of an incident energy analysis to specify PPE is not permitted? Also what is the definition of Site Specific level of PPE indicated under equipment labeling? Are most people moving away from indicating the PPE category on the equipment label?

The revised language states at least one of the following:
• Either the available incident energy with the corresponding working distance or the arc flash PPE category in Table 130.7(C)(15)(A)(b) or Table 130.7(C)(15)(B) shall be listed but not both.
• Minimum arc rating of clothing is required.
• Site-specific level of PPE is required.
Call it instead "Site-specific Level of PPE". As long as you don't call it "PPE Category" there should be nothing preventing you from doing so. Remember that not that long ago people were told not to mix HRC with incident energy. So they began to call it 1, 2, 3 and 4 PPE categories to get away from the term HRC. This time around the NFPA 70E claimed ownership for the term "PPE category" that people moved to, and say you can't use that term with incident energy. Also, the NFPA Handbook shows a sample label with fields to be filled in for "Available Incident Energy" and "Level of PPE" while just half a page earlier states that "available incident energy" cannot be included with the "PPE category" in table 130.7(C)15(A)(b). It makes sense since the "Level of PPE" and "PPE Category" are technically two different terms.