I also do Arc Flash studies at our generating stations, and run scenarios for the different operating configuations. Our labels show the worst case scenario. That way, Operators and/or Electricians don't need to worry about how the system is configured. - See more at:
http://arcflashforum.brainfiller.com/threads/2985/#post-13946 Posting for worst case could possibly make everything Extreme Danger unless worst case is something that can be lived with on a daily basis. If not, then how does an operator and/or electrician perform their functions?
As an extreme example, an operator normally wears non-AR clothing but non-flammable. A motor coupling shears or a pipe breaks and the operator has to rapidly shutdown the equipment at the MCC or Panelboard. However, it is labeled 3.2 cal/cm^2 for worst case operating condition which may be only 1% of the time while 99% of the time it is 0.5 cal/cm^2 In real life would he run to don AR gear or would he just operate the breaker the way he has done for the previous 15 years?
Of course, this whole scenario could loop back to the risk assessment discussions.