| Arc Flash Forum https://brainfiller.com/arcflashforum/ |
| Shock protection - prohibited approach boundary is gone https://brainfiller.com/arcflashforum/viewtopic.php?f=9&t=3593 |
Page 1 of 1 |
| Author: | Noah [ Fri Jan 16, 2015 2:11 pm ] |
| Post subject: | Shock protection - prohibited approach boundary is gone |
Anyone noticed that? Any comments? Wow, we need to revise our label significantly due to the 2015 edition now. |
| Author: | PaulEngr [ Fri Jan 16, 2015 3:16 pm ] |
| Post subject: | Re: Shock protection - prohibited approach boundary is gone |
Yes, it's gone. Shock protection PPE was required previously starting at the restricted approach boundary. No additional requirements existed at the prohibited approach boundary. It was more or less just informational so it was removed as it just served to create confusion. |
| Page 1 of 1 | All times are UTC - 7 hours |
| Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group http://www.phpbb.com/ |