It is currently Wed Oct 28, 2026 8:43 am



Post new topic Reply to topic
Author Message
 Post subject: Panel Question
PostPosted: Thu Dec 10, 2009 7:28 am 

Joined: Thu Dec 10, 2009 7:15 am
Posts: 3
First post here - thanks already for the great info.

I am having trouble finding what I think should be common info. We build "machines" here - and associated "industrial control panels." It's clear these panels should have an Arc Flash label of some sort (per NFPA).

Typical analysis for level of risk includes "available current" for the calculations. Since I usually do not know where or how my panel will be installed, how can I know this info?

Is there a "generic" label I should be using? The "worst-case" label might make routine maintenance impractical.

I hope this post makes some sense! It seems like this would be a common question, but I haven't found the solution yet, so here we are...

Thanks for your help.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 10, 2009 7:41 am 
Sparks Level

Joined: Fri May 01, 2009 9:10 am
Posts: 73
Generic Label

I think the only prudent thing for you would be to affix a generic label in accordance with NEC 110.16. That is pretty much the standard for OEM manufacturers (SqD, Cutler etc.) that I see in the field. The labels can be bought at Grainger, Brady, or pretty much any electrical wholesale house. I believe it is the company's responsibility to assess their equipment. If you are going to install your equipment (in other than dwellings), you will need to follow the safe work practices outlined in the NFPA 70E and wear the appropriate PPE (God forbid you're doing it energized)!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 10, 2009 7:42 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
The arc hazard labels cannot be installed by the manufacturer. As you point out, the manufacturer has no way of determining fault current, let alone incident energy. Generic labels have been applied by manufacturers, but these do not meet the requirements of NFPA 70E-2009. You could provide labels with blanks to be filled in by the customer, but there is no standard format. The format would be different depending on whether or not an IE analysis is performed.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 10, 2009 8:33 am 

Joined: Thu Dec 10, 2009 7:15 am
Posts: 3
Thanks for the quick response.

So - to be clear - as a manufacturer, I am not required to label this equipment. But furthermore - I am not able to assess the risks anyway, unless I visit my machine in the field. This assessment and labeling, then, falls to the end-user.

Is that about right?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 10, 2009 6:50 pm 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
Yes, it's the duty of the end user. You cannot do it (your equipment can be installed elsewhere, the upstream distribution system can be updated). And a generic label with "Don't work live" is still insufficient per NFPA 70E (no Cat and no IE listed).

What you should (must?) put on a label is the AIC your equipment can withstand (along with nominal voltage, amperage, # of phases, frequency, etc.). Note it's not even your duty to verify that end users expose it to something smaller (unless you make it a warranty issue: expose it to too much short-circuit current and the warranty is gone).

Hope it helps you!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 10, 2009 7:38 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
Agree with Vincent totally, but depending on the standards that apply to your equipment you may need to do more from a mfg. perspective.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 14, 2009 9:55 am 

Joined: Thu Dec 10, 2009 7:15 am
Posts: 3
Thanks again, that's all great info.

I do indeed already include all the (previously NEC required) label information (voltage, current...).

The question really arose for two reasons:

a) I've noticed the arc flash label on the competition's machines;
b) The customer asked me to put it on.

I'm thinking "a" is a direct result of "b," but that's really not important. What matters to me is that I do the right thing, and I believe I am, and you have all reinforced my conclusion.

Thanks again!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 14, 2009 10:02 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
CEDEng wrote:
Thanks again, that's all great info.

I do indeed already include all the (previously NEC required) label information (voltage, current...).

The question really arose for two reasons:

a) I've noticed the arc flash label on the competition's machines;
b) The customer asked me to put it on.

I'm thinking "a" is a direct result of "b," but that's really not important. What matters to me is that I do the right thing, and I believe I am, and you have all reinforced my conclusion.

Thanks again!


You should just put a simple label that meets the NEC 110.16 requirements, like this one.


Attachments:
Panel Fault 02.jpg
Panel Fault 02.jpg [ 105.33 KiB | Viewed 5038 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 14, 2009 10:07 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
jghrist wrote:
The arc hazard labels cannot be installed by the manufacturer. As you point out, the manufacturer has no way of determining fault current, let alone incident energy.


You nailed it!

As I recall, there was a proposal for the 2008 NEC Article 110.16 that was going to require more detail on the label and it was rejected for exactly the reason you mentioned here.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 14, 2009 1:37 pm 
Sparks Level
User avatar

Joined: Sun Aug 16, 2009 8:42 am
Posts: 184
Location: Lawrenceburg KY
No arc flash lable may be required, but as a panel builder you may be required to place a label on the panel that contains information below.

Manufacturer name
Supply voltage, phase, frequency, and
full-load current
Short Circuit Current Rating (SCCR)
Enclosure Type

This site has some good panel info. You may already know this but I figured I would throw this out there.

[url="http://www.moeller.net/binary/ver_techpapers/ver959en.pdf"]http://www.moeller.net/binary/ver_techpapers/ver959en.pdf[/url]


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883