PostPosted: Thu Apr 12, 2018 7:52 pm 

Joined: Thu Apr 12, 2018 7:40 pm
Posts: 7
I am working on a model for a double ended sub 13kv/480 that feeds a couple of bus ducts. I’ve set up 5he model to bus duct into 50’ lengths. On each 50’ length I model the bus plugs with a bus and the proper fuse size before adding the cable and then finally a non-motor load to represent for example 480V PDP panel. When I run the evaluation the results don’t go past the fuse/bus plug.

What am I missing?
Should I just model the non-motor load as a bus and select a generic panel from the library?
When do I unline the equipment type and gap in the arc flash table to say switch from a panel to switch gear etc?

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Non-motor loads. What am I missing?
PostPosted: Fri Apr 13, 2018 3:35 am 

Joined: Thu Apr 12, 2018 7:40 pm
Posts: 7
Here is a screenshot of a section of busduct. The non-motor loads are 480v power distribution panels. It appears SKM is not including them in the analysis. Do I need to model a disconnect switch before it? Should I just select the node bus at the impedance change an turn it into a bus/panel and stop the evaluation there?

There is a part of me that is thinking I am going a little too detailed with this by breaking the bus ducts up in 50’ sections and including all the plugs and loads individually as opposed to using an aggregate method. Any direction on this is also highly appreciated

Thanks


Attachments:
F1533BCB-9401-4227-BEAF-413011EB4D95.png
F1533BCB-9401-4227-BEAF-413011EB4D95.png [ 36.45 KiB | Viewed 3658 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Non-motor loads. What am I missing?
PostPosted: Fri Apr 13, 2018 5:10 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Add the panels as busses. They are busses, not loads.

Attachment:
panels.JPG
panels.JPG [ 108.3 KiB | Viewed 3656 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Non-motor loads. What am I missing?
PostPosted: Fri Apr 13, 2018 6:21 am 

Joined: Thu Apr 12, 2018 7:40 pm
Posts: 7
Thanks! That is exactly what I started doing after I thought about it more.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883