| Author: | Canuckeng [ Thu Apr 12, 2018 7:52 pm ] |
| Post subject: | Non-motor loads. What am I missing? |
I am working on a model for a double ended sub 13kv/480 that feeds a couple of bus ducts. I’ve set up 5he model to bus duct into 50’ lengths. On each 50’ length I model the bus plugs with a bus and the proper fuse size before adding the cable and then finally a non-motor load to represent for example 480V PDP panel. When I run the evaluation the results don’t go past the fuse/bus plug. What am I missing? Should I just model the non-motor load as a bus and select a generic panel from the library? When do I unline the equipment type and gap in the arc flash table to say switch from a panel to switch gear etc? Thanks |
|
| Author: | bbaumer [ Fri Apr 13, 2018 5:10 am ] |
| Post subject: | Re: Non-motor loads. What am I missing? |
Add the panels as busses. They are busses, not loads. Attachment:
|
|
| Author: | Canuckeng [ Fri Apr 13, 2018 6:21 am ] |
| Post subject: | Re: Non-motor loads. What am I missing? |
Thanks! That is exactly what I started doing after I thought about it more. |
|