It is currently Wed Nov 11, 2026 5:25 pm
 Post subject: Asymmetrical short-circuit current
PostPosted: Sat Nov 26, 2011 2:26 pm
Hi Guys! How are you?
My name is Wagner, I'm Electrical Engineering student in Brazil.
It's posible use the Asymmetrical short-circuit current for arc flash calculations? Can I use the asymmetrical current like a safety factor?
Wagner. :)
PostPosted: Sun Nov 27, 2011 5:13 pm
Using the asymmetrical short circuit current would be like introducing a very large multiplying factor. If the protective device / arc flash clearing time remained the same as the symmetrical case, then yes this would be conservative and worst case (although I have not heard of anyone doing this). However, using the higher value could lead to a faster protective device operation and lower the overall incident energy.