wilhendrix wrote:
Forum members. This is not an arc flash question, but you have lots of experience and I'd like you're input. We shut off a 2500 amp Square D bolt loc main disconnect switch and it took 2 (good sized) electricians to get the handle moved enough to recharge the closing spring. I'm sure this isn't normal. Has anyone had any experience like this? If so, who did you contact or what did you do to fix the problem?
NFPA70E requires electrical equipment to be properly maintained.
Bolted pressure switches need to be exercised on a fairly regular basis, at least every 3-5 years, or else the grease hardening and dust can cause the moving parts starts to seize. The majority of the time these switches can be cleaned, and even rebuilt. There are manufacturer's service reps as well as independent firms that work on these type of switches on a monthly if not weekly basis. This is a job for experts. Simply spraying everything with a degreaser and lubricant is typically not sufficient.