 Post subject: Extension Cord Fault
PostPosted: Tue Jun 20, 2017 9:38 am 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 40
Using the extension cord as a disconnect for a 1/2HP motor caused the cord to catch on fire. GFCI or circuit breaker feeding the cord did not trip. 120VAC.


Attachments:
File comment: Cord Fault
IMG_0875.JPG
IMG_0875.JPG [ 1.45 MiB | Viewed 33253 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Extension Cord Fault
PostPosted: Mon Jun 26, 2017 8:21 am 

Joined: Wed Dec 21, 2011 5:00 pm
Posts: 10
Probably caused by excessive resistance at plug vs. over amperage. This would result in more heat than could normally be dissipated by the plug until it ignited.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Extension Cord Fault
PostPosted: Mon Jun 26, 2017 8:28 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 619
Location: Wisconsin
BarryB wrote:
Probably caused by excessive resistance at plug vs. over amperage. This would result in more heat than could normally be dissipated by the plug until it ignited.


Yeah, and there appears to be little to no damage around the ground pin, so it looks like a GFCI might not have noticed this event at all.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883