It is currently Wed Nov 11, 2026 2:17 am
 Post subject: Lock-out relays
PostPosted: Fri Dec 04, 2009 2:24 pm
Hi everyone,
I am doing an arc flash study for a generating station that protects the main generator buses through lockout relays (i.e. 50/51/87 etc. element actuates the 86 element which in turn initiates the circuit breaker trip coil). It turns out there is a wide variance of activation times on these lockout relays (from reading on-line specs) and it is not particularly easy to get this data from the client. How does everyone incorporate the 86 element time into their model? I have heard times ranging from 130ms all the way down to 8ms... makes a pretty big difference in HRC.
Thanks in advance for the input.
Tim Ricard
PostPosted: Fri Dec 18, 2009 11:21 am
Electroswitch says .5 cycle.