 Post subject: Dynamic Arc Reduction systems
PostPosted: Tue Dec 24, 2024 2:26 pm 
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 174
We recently did an arc flash study on a new Siemens 3000 amp 480 volt system. The switchboard came with Siemens’ new Dynamic Arc Reduction system preinstalled. The sort of thumbnail version of what the DAS does is to reset the main breaker so it trips at a much reduced current and time. I asked Siemens representatives this question: if there’s a short at the line side of the main breaker, what does the DAS do? Here is my concern. An electrician decides to open the cabinet and do some testing with the gear left on. He switches on the DAS and assumes he can now wear very low calorie PPE instead of 100 calorie PPE the line side has. He relies on the DAS to greatly reduce the hazard, but there is a line side fault at the main. I doubt this specific scenario may happen, but it is still possible. I’d appreciate your thoughts on this considering the fact that switchboards have few if any internal barriers to slow or stop an arc.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Dynamic Arc Reduction systems
PostPosted: Fri Dec 27, 2024 8:43 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 599
Location: Wisconsin
wilhendrix wrote:
We recently did an arc flash study on a new Siemens 3000 amp 480 volt system. The switchboard came with Siemens’ new Dynamic Arc Reduction system preinstalled. The sort of thumbnail version of what the DAS does is to reset the main breaker so it trips at a much reduced current and time. I asked Siemens representatives this question: if there’s a short at the line side of the main breaker, what does the DAS do? Here is my concern. An electrician decides to open the cabinet and do some testing with the gear left on. He switches on the DAS and assumes he can now wear very low calorie PPE instead of 100 calorie PPE the line side has. He relies on the DAS to greatly reduce the hazard, but there is a line side fault at the main. I doubt this specific scenario may happen, but it is still possible. I’d appreciate your thoughts on this considering the fact that switchboards have few if any internal barriers to slow or stop an arc.


This is a safety training issue. A qualified person would no the zone of protection of the "DAS".
Additional signage/warning labels may be of help.

Training should also emphasis that PPE is the last level of protection. PPE does not guarantee no injuries, only that the injuries received are not likely to be fatal.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Dynamic Arc Reduction systems
PostPosted: Sat Dec 28, 2024 4:34 pm 
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 174
Thank you for your comments. Any thoughts on the question of arc reduction in switchboards verses switchgear?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Dynamic Arc Reduction systems
PostPosted: Mon Dec 30, 2024 1:40 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 599
Location: Wisconsin
wilhendrix wrote:
Thank you for your comments. Any thoughts on the question of arc reduction in switchboards verses switchgear?

A device cannot protect itself, it needs to be 'remote' or upstream, especially in switchboard and MCC construction with n0n-compartmentalized bus.

It might work in switchgear where the bus is completely compartmentalized. You would need to perform a risk analysis.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Dynamic Arc Reduction systems
PostPosted: Sat Jan 04, 2025 9:32 am 
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 174
JBD, I agree. Seems to me switchgear would be fine with DAS, but not so sure about switchboards.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Dynamic Arc Reduction systems
PostPosted: Fri Sep 05, 2025 11:12 am 

Joined: Wed Mar 16, 2022 7:10 am
Posts: 4
My understanding, unless there is a barrier to separate the line side section from the load side, the incident energy is not to be reduced to a lower level within the board even it is equipped with a DAS.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Dynamic Arc Reduction systems
PostPosted: Tue Sep 09, 2025 5:48 am 
Sparks Level

Joined: Fri Sep 28, 2018 7:32 am
Posts: 55
Location: Sioux Falls, SD
Agreed. A major item here is personnel training, potentially including equipment labeling. First someone must program the DAS to ensure it functions. I have seen ERMS/ARMS systems installed all over because "code requires it" but upon analysis, the feature does not provide any benefit. Once DAS is setup personnel must be trained on when to activate it and what its zone of coverage is. It will not have an impact on the hazards upstream of it...i.e. the line side of the main breaker. If compartmentalized/isolated, DAS at the main breaker may lower the hazard for the rest of the panel. Otherwise, it "may" lower the hazard at downstream equipment. Again, this must be assessed as I have seen multiple units installed that are unable to make any impact on the arc flash hazard.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883